grounding/ wiring up a single bushing piglet.........
Posted by dave on 11/30/2004, 8:54 pm
|
Re: grounding/ wiring up a single bushing piglet.........
Posted by Bert Hickman on 12/1/2004, 12:16 am, in reply to "grounding/ wiring up a single bushing piglet........." Hello Dave, Does your piglet have 3 lugs on the low voltage side (X1, X2, and X3)? If so, the center tap of the LV side may be internally connected to the core and case. Disconnect all voltage inputs to the LV side and check for continuity between one of the X lugs (it doesn't matter which) and the case. If you measure continuity you'll need to disconnect this internal connection so that you can run the pig properly with a ballast from a 240 volt source while keeping the case at earth potential. Best regards, -- Bert --
|
Re: grounding/ wiring up a single bushing piglet.........