Jacobs Ladder
Posted by mario occhipinti on 12/10/2003, 9:41 pm
|
Re: Jacobs Ladder
Posted by Bert Hickman on 12/10/2003, 10:04 pm, in reply to "Jacobs Ladder" Mario, If the center tap of the LV winding is connected only to the center LV feedthrough lug (X2) on the transformer's case and not to the core, then you may not need to do anything more. However, verify that this is the case by measuring continuity between the LV center tap (X2) and the case of the transformer using an ohmmeter or continuity checker. If these two points are not electrically connected then you can simply leave the transformer's LV center tap terminal (X2) unconnected and connect the case of the pig to ground. Good luck and best regards, -- Bert --
|